Zone HVAC:IdealLoadAirSystem and Zone Latent Cooling Result

Hello Everyone, May I ask why I got latent cooling so high at first, remained constant, and then rose again. Both supply air latent and zone latent have the same trend. (https://www.dropbox.com/scl/fi/3xsim7...) (https://www.dropbox.com/scl/fi/jgvey9...) I have two internal gains objects: People, Lighting (operate at the same time with HVAC from 9am-6pm) Infiltration is 2ACH open 24hr, Outdoor Air is flow/person (0.00944m³/s using occupancy schedule) Thermostat at 24'C (https://www.dropbox.com/scl/fi/be2kvh...) Here is my model (https://drive.google.com/drive/folder...)

Thit's avatar
55
Thit
asked 2024-09-03 08:21:48 -0500, updated 2024-09-06 00:59:57 -0500
edit flag offensive 0 remove flag close merge delete

Comments

@Thit can you upload your EnergyPlus model to Google Drive, Dropbox, etc. and then share a link to that? That would allow others to provide better help.

Aaron Boranian's avatar Aaron Boranian (2024-09-03 09:37:25 -0500) edit
add a comment see more comments

1 Answer

3

Good question. The HVAC system starts up at 0900 with high latent load (ie. outside drybulb is low, humidity is high). HVAC system gets humidity and temperature under control and begins steady state operation. Later in the day, right before the HVAC system shuts down at 1800, humidity begins to increase, so the HVAC system latent load increases.image description

Ski90Moo's avatar
869
Ski90Moo
answered 2024-09-08 15:25:13 -0500
edit flag offensive 0 remove flag delete link

Comments

@Ski90Moo thank you sir

Thit's avatar Thit (2024-09-09 07:56:41 -0500) edit