undersized HVAC system in CBECC-Com

What is the process for compliance when CBECC-Com determines the HVAC system for the proposed building is undersized?

NORESCO's avatar
341
NORESCO
asked 2014-11-04 18:51:35 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-03-10 10:50:23 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

When the simulation has more than 150 hours of unmet load hours, the HVAC system capacities must be manually increased to meet the load. Remember to increase both airflow and coil capacities. There is an exceptional condition that should be marked “Yes” when this is done, and a note will be added to the compliance report.