EnergyPlus SEER Standard vs SEER User

Hi,

In the table results in E+, there are outputs for SEER values. One is "SEER Standard", and one is "SEER User".

Any idea what the differences are? They give slightly different values.

Cheers

Sebastien Brideau's avatar
73
Sebastien Brideau
asked 2024-06-12 15:02:30 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-06-12 15:22:29 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

You can generally find details for EnergyPlus summary report tables in the Input Output Reference section for the Output:Table:SummaryReports object type that generates the summary reports file. For SEER, there only seems to be one Equipment Summary section table that generates data, and the main difference is that:

The SEER value is calculated using user specified Part Load Factor (PLF) curve used for energy performance calculation and the SEER Default value is calculated using the AHRI Standard 210/240-2008 default PLF curve and cooling coefficient of degradation value of 0.25.

I assume that "SEER User" and "SEER Standard" that you mentioned are "SEER" and "SEER Default" in the description above, respectively.