How to use setpoints for controlling the zone return temperature?

I'm modelling a single zone air loop which is cooled using a cooling coil. I can use a setpoint to control the temperature which leaves the cooling coil, but I'm more interested in controlling the temperature that leaves the zone (and thus enters the cooling coil).

I tried:

  • Putting a "SetpointManager:Scheduled" on this node, but I get an error that not all nodes have a setpoint attached.

  • Putting setpoint manager on the leaving and entering nodes, but then the entering node overwrites the leaving node.

Anybody who knows how to solve this?

Pepijn's avatar
11
Pepijn
asked 2024-06-12 09:22:49 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-06-12 15:04:14 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

I may be completely mistaken about what you wish to accomplish, but the temperature leaving the zone should be pretty close to the zone temperature itself. And that is controlled via the zone's thermostat and the setpoint schedule assigned to the thermostat. So I would make sure the zone has a thermostat and the thermostat has a setpoint schedule.

mattkoch's avatar mattkoch (2024-06-18 19:52:49 -0500) edit