CBECC-Com terminal units error

My project is using packaged single zone rooftop units. When I enter my systems and attempt a compliance analysis, I get an error message that terminal units are required. My project doesn't have terminal units. What is the problem?

NORESCO's avatar
341
NORESCO
asked 2014-11-04 18:46:47 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-10 21:07:59 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Terminal units are required by EnergyPlus as the connection between an air system and a thermal zone. In your case the terminal units would have a type of "Uncontrolled" and corresponds to the grill through which supply air enters the space.