Setpoint Managers not showing up

I am editing a building that had hvac air loops controlled by setpoint manager scheduled. I have been trying to change them to a setpoint manager follow system node temperature. After I delete the existing setpoint manager and replace it with the desired one, the system does not recognize a setpoint manager. Although it's visible in the layout, if I go to the control tab in Openstudio, it says "Unknown or missing supply air temperature control. Try adding a setpoint manager to your system."

Is there something I need to enable to change the setpoint manager? I've tried a few other types of setpoint managers as well and they also don't seem to register.

image description

clima337's avatar
51
clima337
asked 2024-03-26 20:13:50 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-03-27 09:37:02 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

You can ignore it. This is just trying to helpful, but there are only the 4 most common SPMs that are handled by that view:

  • SetpointManager:Scheduled
  • SetpointManager:SingleZoneReheat
  • SetpointManager:OutdoorAirReset
  • SetpointManager:FollowOutdoorAirTemperature

Anything not in that list but still allowed by E+ will still work.


I filed an enhancement request at openstudiocoalition/OpenStudioApplication#708