Modeling an inverter based AC as a VRF

I modeled the inverter based AC as a VRF, but the simulated VRF energy consumption values are much higher than measured values of the inverter based AC. I tried changing the partload ratio curve coefficients because the load in the room is very small. It did not work. any suggestions?

hk65's avatar
11
hk65
asked 2024-03-20 02:37:29 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-03-20 15:26:45 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Probably should be using cycling fan mode and also check the cooling EIRfPLR curve to make sure it represents the VS compressor energy. VRF will use a different curve. See figure 10 in https://www.fsec.ucf.edu/en/publicati.... The VS AC EIRfPLR curve will go lower than the one shown in the figure (blue line) and cross at 0,0.

rraustad's avatar
13.8k
rraustad
answered 2024-03-20 15:34:34 -0500