DOE Reference building HVAC

I am looking through DOE reference building IDFs. Using the Notepad++ comparison tool, I am finding differences between reference building HVAC equipment characteristics (e.g. DX coil Rated COP or Package Fan Efficiency). I know that simulations preform a sizing run first and then the actual simulation, so I am wondering why these parameters may differ? I am comparing the same building types but for different climate zones, so it may be solely weather based. However, I am wondering if there could be another rationale. Why would these parameters differ before the sizing run occurs?

FrontierAssoc104's avatar
503
FrontierAssoc104
asked 2015-07-30 16:04:40 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2015-07-30 17:03:13 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Equipment efficiencies in the reference building models are determined according to energy standards, and are based on equipment size. Likely the differences you're seeing is due to the previously auto-sized equipment capacities in different climate zones yielding a different equipment efficiency as specified in the energy standard.

The efficiencies for different systems and capacity ranges is documented in the Commercial Reference Buildings report, starting on page 35.