HVAC IdealLoadsAirSystem output metric

Hi!

I'm using EnergyPlus v23.2.0 to model a building and determine the amount of energy needed when I apply different natural ventilation strategies. To mesure the theorically energy demand that I must to provide to get a confort temperature I'm using the HVACTemplate:Zone:IdealLoadsAirSystem.

In the documentation I found that this template is preprocessed and transformed into a ZoneHVAC:IdealLoadsAirSystem object. But here I have a question. The documentation also indicate that the meters for the Template are DistrictHeating and DistrictCooling (InputOutputReference v23.2.0 p. 2530), and for the ZoneHVAC are DistrictHeatingWater and DistrictCooling (InputOutputReference v23.2.0 p.1269). So, which meter I must to use to calculate the energy demand? Heating:DistrictHeatingWater and Cooling:DistrictCooling or Heating:DistrictHeating and Cooling:DistrictCooling.

Thanks!

hermmanhender's avatar
243
hermmanhender
asked 2024-02-25 05:41:37 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-02-26 10:44:22 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

DistrictHeating was renamed to DistrictHeatingWater in EnergyPlus 23.2. You can confirm this by running the simulation and looking at the *.mdd output file. I have posted a bug report here about the fact that there are still lingering references to the old name.

shorowit's avatar
11.8k
shorowit
answered 2024-02-25 11:33:34 -0500, updated 2024-02-25 11:34:50 -0500
edit flag offensive 0 remove flag delete link

Comments

Perfect, thank you very much!