How to report actual total autosized capacity of HVAC system (not just based on sensible load)?

Hello,

I am simulating a medium office building with VAV packaged A/C unit with reheat. After the building simulates, I am viewing the tabular output report. In that report it gives a "HVAC Sizing Summary". This auto-sizing summary gives calculated sensible design load (No ventilation or latent load included).

So my question is, what is the actual full auto-sized capacity of the equipment the simulation uses and how do I report it?

The simulation can't use the sensible only load as equipment size, as that would result in a severely undersized cooling/heating system with a lot of unmet hours. My initial guess would instead be to use the reported auto-sized cooling and heating coils' capacities in the coil sizing summary.

Also, is there any reasoning for why it gives sensible load only and not include latent or ventilation loads? Seems misleading, but perhaps I am missing something! Thanks for any information on this :)

eklein1317's avatar
21
eklein1317
asked 2024-02-23 17:55:01 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-02-26 10:39:21 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

I am looking at the HVAC Sizing summary in the latest version of EnergyPlus and I do see "total" coil capacity. Depending on the type of coil the report may show only sensible so it would be determined by your input file configuration. If you could post a picture of the table in question, and the version of E+ you are using, it would be easier to understand what you see in those tables.

image description

rraustad's avatar
13.8k
rraustad
answered 2024-02-26 10:32:22 -0500