I am getting error like - In calculating the design coil UA for Coil:Cooling:Water

for more detailed error message -

** Warning ** In calculating the design coil UA for Coil:Cooling:Water THERMAL ZONE: A013 COOLING COIL
**   ~~~   ** the outlet chilled water design enthalpy is greater than the inlet air design enthalpy.
**   ~~~   ** To correct this condition the design chilled water flow rate will be increased from 2.49319E-006
**   ~~~   ** to 6.01354E-006 m3/s
** Severe  ** Calculation of cooling coil design UA failed for coil THERMAL ZONE: A013 COOLING COIL
**   ~~~   **   Bad starting values for UA
**   ~~~   **  Coil design UA set to 245.887736 [W/C]

Any ideas on how to fix this?

Yagnik's avatar
41
Yagnik
asked 2024-02-21 07:58:53 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-02-21 11:19:15 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

It may be that the Sizing:Zone Zone Cooling Design Supply Air Humidity Ratio is higher than what is calculated for the coil inlet air humidity ratio (i.e., mixing return air and outdoor air)? You could try lowering the Sizing:Zone cooling supply air hum rat. Also try lowering the same variable in the Coil:Cooling:Water object if the Sizing:Zone change does not work. It looks like this warning needs more information so the user can figure out what is wrong (e.g., inlet air temp, inlet air hum rat, outlet air temp, outlet air hum rat, etc).

rraustad's avatar
13.8k
rraustad
answered 2024-02-21 11:35:28 -0500