Internal load assumptions - BEopt

Does BEopt consider the internal loads (e.g. occupants) in the annual heating and cooling load calculation? if yes, How? and How can I modify it?

m.karimi431@gmail.com's avatar
61
m.karimi431@gmail.com
asked 2024-01-14 22:52:32 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-01-15 09:17:02 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

BEopt calculates internal gains from plug loads, major appliances, lighting, water heater tank losses, etc., all of which affect the heating/cooling load calculations. When BEopt is told how many occupants there are, all of these individual items are adjusted accordingly. (When BEopt is not told how many occupants there are, say for new construction, it uses the number of bedrooms as a proxy for the number of occupants.)

You can modify any of the individual items that contribute to internal gains, though the miscellaneous "Plug Loads" category is one of the biggest knobs available to you.