Hello, I have the following error in open studio.

As attached in the image in february the temperature is lower than in december, but the heating consumption is higher in december. This does not make sense.

Does anyone know why?

image description

Pablocm's avatar
55
Pablocm
asked 2023-11-25 15:55:54 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-11-27 09:33:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

For non-leap years, February has 3 less days than December. Based on your results, the average daily heating load in February (28 days) is 11.42 kWh/day, while the average in December (31 days) is 11.47 kWh/day (at 20 cents/kWh, that's roughly 1 cent/day).

In addition, February typically has more sunlight than in December (Northern Hemisphere):

image description

This would be enough to tilt the balance towards less heating in February than in December in many locations and for many building types. This would not be the case everywhere; in my (much colder) neck of the woods, it is on average ~5K colder in February than in December; despite being sunnier, it is not unusual to heat more in February (than in December). This is just scratching the surface ...