Humidity setpoint not met

Hi everyone, I'm new to BEM and OpenStudio. I have made a model to calculate ideal loads of a building. I set humidification and dehumidification setpoints in OpenStudio, creating percentage schedules, but after running the simulation I see that the zone air relative humidity is out of my range in many hours. Can anyone suggest what am I doing wrong? Consider that I am new to this world there could be some trivial errors.

EDIT: Also, is there a way to show latent cooling as hourly variable?

Thanks! Model LINK HERE

image description

therealtorte's avatar
13
therealtorte
asked 2023-11-24 09:13:40 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-11-27 09:25:33 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

I would suggest plotting zone dew point rather than zone relative humidity, as, on a psychrometric chart, relative humidity varies with dry bulb. There are many parts to this one question: operation of humidifiers in the winter, off-coil temperature in cooling, how airflows were sized, what controllers and sensors exist... How does the building in real life monitor and control to relative humidity?