Problem of humidity control in the 5ZoneCoolingPanelBaseboard.idf example [closed]

Hi everybody,

I am trying to make a air loop with a water coil to control the humidity. I found the 5ZoneCoolingPanelBaseboard.idf case in the energyplus example. It is said in this example that the humidity is control to be below 50% for the space 2-1. This is normally done with a humidistat and a set point manager. But when we run and check the results of this example, the humidity is not controlled and part time over 50 %. image description.

Is it normal ?

looooic's avatar
79
looooic
asked 2023-10-23 07:50:23 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by looooic 2023-10-24 02:50:28 -0500

Comments

add a comment see more comments

1 Answer

0

This works well, actually there is a schedule that makes work the humidity control only during the day.