Hi all,

I was wonderring if anyone knows what is the reference pressure for Air Change per Hour (ACH) under ZoneInfiltration:DesignFlowRate object.

More specifically, for AirChanges/Hour field, is the pressure difference based of 4 Pascals ACH or 50, ?

Thanks, Mohammad

Mohammad's avatar
330
Mohammad
asked 2023-10-11 12:03:24 -0500, updated 2023-10-11 20:51:37 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The ACH should reflect expected pressure differences across the building envelope during normal occupation/operation (just like the 4x other "Design Flow Rate Calculation Methods"). So yes, closer to 4Pa (than 50Pa or 75Pa).