Unexpected results in energy consumption with HVAC-template ideal load air system

I am analyzing the results of two idf files with ideal loads using hvac-template and hvac-detailed.

I am finding unexpected results. I am considering the original location (Buffalo, NY, USA), which has a winter-dominated climate. However, the ideal load for cooling (257.92 GJ) is 2.3 times larger than that for heating (111.28 GJ). On the other hand, for the idf with HVAC-detailed, the energy for heating (225.11 GJ) is much larger than that for cooling (70.95 GJ), which seems to be far more reasonable than the results for ideal loads.

I wonder what is happening and why??

Moheete's avatar
113
Moheete
asked 2023-09-14 03:18:30 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-09-14 09:29:15 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Perhaps your ideal air system is doing dehumidification? See the Dehumidification Control Type input for the HVACTemplate:Zone:IdealLoadsAirSystem object. As the documentation explains, "The selected dehumidification control type is always applied when the unit is in cooling mode."