Chiller Evaporator Cooling Rate

Hi,

I model a building in OpenStudio and try to compare the hourly chiller evaporator cooling rates between actual and modeled chillers. It seems like the modeled outputs have jumping values during the first hours as shown in the chart. I use the OS:Chiller:Electric:EIR class to model the chillers. I am not sure whether this is common or it's an error from my inputs. Could anyone please recommend some methods to deal with these first-hour spikes?

Thank you.

image description

Om's avatar
49
Om
asked 2023-08-16 02:21:55 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-08-16 09:12:10 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

It seems to me that there is a thermal inertia at the beginner of each day in the modeled chiller. The modeled chiller has to work more to overcome this load and then cooling demand it is less than the Actual one.

It could be interesting if the area under the curve (cooling energy) of each case is the same.