Custom Meter Error

I m trying to add a custom meter to "Zone Ideal Loads Supply Air Total Cooling Energy" in Open studio Application using a measure. It doesn't work. It says pervious meter specification caused error, any help?

Jay86's avatar
1
Jay86
asked 2023-05-23 18:02:39 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-05-24 09:16:36 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

"Zone Ideal Loads Supply Air Total Cooling Energy" is an output variable, not an output meter. If you run the simulation without any output requests, you can find the full list of available output meters in the eplusout.mdd file and output variables in the eplusout.rdd file.

shorowit's avatar
11.8k
shorowit
answered 2023-05-24 17:06:11 -0500