Why ZoneHVAC:Baseboard:RadiantConvective:Water has an air loop?

Hello all,

I want to simulate a simple single zone room with a single radiator unit with District Heating supplying the hot water to it. I want to use ZoneHVAC:Baseboard:RadiantConvective:Water. However, in the documentation I read that in addition to the hot water loop, there is an air loop with an air inlet and outlet node. I can not imagine it physically, how a radiator unit has an air loop. Has anyone simulated similar system before?

Thanks in advance.

nagpalh's avatar
75
nagpalh
asked 2023-02-09 13:17:18 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2023-02-13 11:00:28 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

(original comment now posted as an answer).

Denis Bourgeois's avatar Denis Bourgeois (2023-02-09 15:05:48 -0500) edit

I agree with Denis, you should turn that comment into an answer.

Julien Marrec's avatar Julien Marrec (2023-02-10 02:37:59 -0500) edit
add a comment see more comments

1 Answer

3

The baseboard object output (not input) variables do include air inlet and outlet temperatures in degC. I suspect the inlet is simply the zone air temperature, the outlet: air temperature coming out of the baseboard. But I see no mention of an optional/required air loop. Am I misunderstanding your question? ... an answer (as suggested by Julien), originally posted as a comment.

Denis Bourgeois's avatar
2.8k
Denis Bourgeois
answered 2023-02-10 05:50:12 -0500
edit flag offensive 0 remove flag delete link

Comments

Or perhaps the baseboard's input field for inlet node name was confused for an air inlet node when it's actually for a water inlet node?

Or something was misleading from the Engineering Reference?

@nagpalh can you share a link to the EnergyPlus web docs where you read an air loop is needed for the baseboard?

Aaron Boranian's avatar Aaron Boranian (2023-02-10 08:48:35 -0500) edit

@Denis Bourgeois @aaron Yes, the object does not need an air loop to be defined. However, I was confused because of the output variables which report Baseboard Air Inlet Temperature, Baseboard Air OutletTemperature and also Baseboard Air Mass Flow Rate. I couldn't understand where does these variables come from?

nagpalh's avatar nagpalh (2023-02-11 09:14:19 -0500) edit