2

multiple air conditioners BEOPT

How do I simulate multiple air conditioners in BEopt? Does BEopt support multiple thermal zones?

thanks a lot

lihao2004's avatar
51
lihao2004
asked 2022-10-28 09:07:52 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2024-03-20 15:26:53 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

BEopt doesn't explicitly allow modeling multiple air conditioners, but you can approximate it by using the average efficiency (weighted by the floor area served by each AC). Unless you override it, BEopt will automatically autosize the AC to meet the entire cooling load, even if that means the capacity is larger than whatever the largest residential AC on the market is. You'll likewise want to enter average duct leakage/insulation inputs.

Note: There is no need for multiple thermal zones just because there are multiple air conditioners, since all finished/conditioned space will be maintained to the same setpoint.