1

Is there a way of modeling fixed outdoor air fraction for VAV systems in CBECC-Com?

My hunch is that this is only possible through the Exceptional Design Compliance process, but I just wanted to see if there was a way of doing this within CBECC-Com.

I'm looking to model fixed outdoor air fraction for a system that varies supply airflow (the design OA is greater than the minimum required). My assumption is that CBECC-Com defaults to providing the design outdoor air at all times regardless of the supply airflow rate.

anchapin's avatar
626
anchapin
asked 2015-06-05 08:08:52 -0500
edit flag offensive 0 remove flag close merge delete

Comments

I'm going to try to use the Scheduled option for the Outside Air Control Schedule Method input and set the min fraction sch to be the outdoor air fraction.

anchapin's avatar anchapin (2015-06-05 08:24:07 -0500) edit

After adding the min fraction schedule, I found out that this Outside Air Control Schedule Method is not allowed for compliance analysis simulations.

anchapin's avatar anchapin (2015-06-05 12:59:07 -0500) edit
add a comment see more comments

1 Answer

2

This appears to not be an allowed input for compliance analysis.

anchapin's avatar
626
anchapin
answered 2015-06-05 12:59:37 -0500
edit flag offensive 0 remove flag delete link

Comments

Yes, you are correct, CBECC does not currently support modeling fixed OA fraction systems. If you feel that this capability is important, I recommend submitting an 'Other' issue and specify it as a feature request: http://bees.archenergy.com/issue.html This will allow us to formally track it as a possible feature for future versions.

DavidReddy's avatar DavidReddy (2015-06-05 19:08:49 -0500) edit
add a comment see more comments