Can I schedule chiller off or on at anytime in Openstudio

Can I schedule chiller off or on at anytime in Openstudio? Because the chiller is not working all the time. Thank you

Abee's avatar
41
Abee
asked 2022-06-01 03:19:54 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2022-06-01 09:50:43 -0500
edit flag offensive 0 remove flag close merge delete

Comments

This is a difficult question that I looked into once before. Because the chiller loop is scheduled, not the individual chillers, I think you would have to put the chiller on it's own separate loop. Then, attach it to the main chilled water loop via a heat exchanger. You could make the heat exchanger 100% efficient. You will have to somehow coordinate the setpoint managers for both chiller loops.

Ski90Moo's avatar Ski90Moo (2022-06-03 11:38:08 -0500) edit
add a comment see more comments