Thermal Loads inside Open Studio and Energy Plus Results

Hi Everyone,

In the Open Studio result *.HTML, I get a big difference between the load calculations and the system size. Almost double. I need to clarify that the model doesn’t have any ventilation/economizer or infiltration rates ( For testing proposes). Using SZ Heatpump my open studio output defines some Minimum and maximum Outdoor air. Why there is a Maximum if everything is set to zero. This is possible to view "Controller:OutdoorAir" (https://drive.google.com/file/d/1fKjk...)

Also, the load is specified as hardcoded. I would like to understand better the source of this number and how it gets calculated.

Thanks!

enriquesissa's avatar
31
enriquesissa
asked 2022-04-17 04:16:05 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2022-04-17 08:05:11 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The sensible table only shows sensible loads associated with the space. The HVAC system sizing can include outside air loads, fan heat loads, efficiency penalties, latent heat loads, standby losses, and parasitic loads.

Also see this thread: https://unmethours.com/question/60419...

Ski90Moo's avatar
869
Ski90Moo
answered 2022-04-18 10:55:13 -0500
edit flag offensive 0 remove flag delete link

Comments

But double the sensible? I defined zero infiltration or Outdoor air. Also Is there any way to see the breakdown?