In the Library of Openstudio, I found there is no component for air-source heat pump. So how should I model an VAV system with ASHP in OpenStudio?

(Btw, I see a measure called 'Aedg Office HVAC ASHP DOAS' in Library but I just cannot apply it successfully. If the measure can be used I think it's also an approach.)

Thx in advance!

shmily_world's avatar
133
shmily_world
asked 2021-12-27 20:26:50 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2022-02-23 12:17:34 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

I have used the openstudio-standardsimplementation. You can create a measure (or use a ruby file, IRB). I have pasted below some code.

require 'openstudio'
require 'openstudio-standards'

model = # load the existing model somehow

template = '90.1-2016' # or whatever
standard = Standard.build(template)


hot_water_loop = model.getPlantLoopByName('Hot Water Loop').get

standard.create_central_air_source_heat_pump(model,
    hot_water_loop,
    name: nil,
    cop: 3.65)

model.save(path,true)

You can find the source code for the implementation here.

Luis Lara's avatar
2.1k
Luis Lara
answered 2021-12-30 01:42:45 -0500
edit flag offensive 0 remove flag delete link

Comments

Hi thank you so much! I will do further try. Is it a OpenStudio measure or an EnergyPlus measure?

shmily_world's avatar shmily_world (2022-01-04 01:18:12 -0500) edit

If you create it, this would be an OpenStudio measure

Luis Lara's avatar Luis Lara (2022-01-04 15:11:44 -0500) edit