VAV Reheat with Humidifer

I'm modeling humidity control of Data Center in Office Building. RH need to be controlled as 40%~60% in Data Center, 50% and lower in other zones occupied. A VAV reheat system control every floor, for 5 zones occupied, and 1 data center. Desiccant system has been set in every VAV airloop to dehumidification, but for terminal, only one zone(data center) need humidifer, but when I put it after reheat coil of data center, some errors occured. So how can I reach this target?

Cold wong's avatar
67
Cold wong
asked 2021-12-05 00:24:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

EnergyPlus can model 17 different types of air terminal units, but they are all preset for specific configurations (reheat vs. no reheat, constant volume vs. variable volume, etc.). None of these configurations include a humidification coil. Also, the Engineering Reference section for humidifiers doesn't mention any limitations on where they can be placed (central air system, outdoor air system, single-zone HVAC, etc.).

So, you're options are to:

1) Place a humidification coil at the outlet of the air terminal unit. The outlet node from the humidification coil is now the inlet/supply node for the zone. It sounds like you have already tried this.

2) Instead of placing the humidifier after the terminal, use a single-zone HVAC component in EnergyPlus that can contain a humidifier. It would then humidify "in parallel" to the VAV system supply air. I found one for containing a dehumidifier, but not a humidifier.

3) If those both don't work, place the humidifier in the central air system serving the data center. If the other occupied zones on the same floor as the data center don't need a humidifier, then you can create a separate VAV airloop for the data center on each floor.

Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2021-12-05 08:43:24 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks, that's what I'm looking for.

Cold wong's avatar Cold wong (2021-12-05 08:46:25 -0500) edit

I want to konw if EnergyPlus could simulate two AirLoops in one zone, if not, is theZoneHVAC:EvaporativeCoolerUnit a good choice?

Cold wong's avatar Cold wong (2021-12-05 08:56:23 -0500) edit

Yes, EnergyPlus can simulate multiple air systems serving one zone. You can read more in this post.