How to increase the heating load for a low rise apartment building with 6 units?

I am using Open studio for energy modelling. I have added 3 packaged roof top units for 6 apartments in my building. I have added 2 apartments per RTU. My heating load should be around 120000kBtu but I am getting only 10000kBtu which is very low for occupancy of 24-30 people. I have changed many times and checked parameters. Let me know which parameter i need to look for and edit to get the value. I am using default settings for now.

fatima2.khan's avatar
41
fatima2.khan
asked 2021-10-15 12:43:33 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2021-10-18 08:50:05 -0500
edit flag offensive 0 remove flag close merge delete

Comments

@fatima2.khan what simulation tool are you using? Please mention it in the title or body of your post, as well as add a tag for the tool so that others can provide better help.

Aaron Boranian's avatar Aaron Boranian (2021-10-15 15:14:11 -0500) edit

I am using Open Studio.

fatima2.khan's avatar fatima2.khan (2021-10-17 21:12:01 -0500) edit
add a comment see more comments

1 Answer

0

I would start by double checking your Infiltration and more importantly the mechanical ventilation / outdoor air.

Ensure that you are using DesignSpecification:OutdoorAir (those are best set at the SpaceType level), and correctly setting parameters on your AirLoopHVACOutdoorAirSystem and Controller:OutdoorAir objects for each loop (especially if it's a DOAS with 100% outside air, you need to force the Minimum Outdoor Air schedule of the Controller:OutdoorAir to always on.

Request Output:Variables to check that your zones are getting the correct amount of outdoor air at all times.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2021-10-19 03:08:25 -0500, updated 2021-10-19 03:11:05 -0500