Load vs Demand vs Consumption [ESL question]

Hi, everyone! English is a second language for me so distinctions between those terms are a bit confusing to me.

Here are my assumptions for heating period so far:

Heating load - is the amount of energy a space with occupancy and plug loads needs to receive in winter to maintain its temperature within set points (no air changes or re-circulation or anything else; mostly energy transfer except for infiltration).

Heating demand - is the amount of energy an HVAC system will provide to condition that space and to condition outdoor air before supplying it to the space.

Heating consumption - is the amount of energy that will be consumed by that HVAC system to satisfy the heating demand. [If the system uses only electric heaters then demand = consumption; if the system uses heat pumps then demand > consumption).

Are my assumptions reasonable? Please, correct me where I am wrong.

My follow up question would be: where can I see each of these values in the DesignBuilder simulation report? Or EnergyPlus report?

Thanks!

Kirill Fedtsov's avatar
157
Kirill Fedtsov
asked 2021-10-01 11:28:28 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2022-02-08 09:12:53 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Hi. I am quite sure that heating load doesn't take in to account people or plug loads. Heating load is used to size the heating equipment therefore you have to take the worst case scenario.

Heating demand is the energy rate (kW) that you need to maintain inside design conditions. This output takes into account internal loads.

Heating consumption is the energy used so heating demand multiplied by time.

I hope I am correct.