First time here? Check our help page!
1

is there a measure to assign constructions based on different climate zone

is there a measure to assign constructions based on different climate zone

Rwadhwa910's avatar
383
Rwadhwa910
asked 2021-08-12 17:01:46 -0600
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2021-08-17 11:21:47 -0600
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The Space Type and Construction Set Wizard will do this. It has an option to skip or include both space types and constructions, so you can include constructions but not space types if you would like to. It has an argument for target standard and climate zone. Note that this will set a default construction set for the building. If you have constructions assigned to spaces or surfaces, they will override the building default. There is a measure to remove hard assigned constructions if needed.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2021-08-13 15:15:46 -0600
edit flag offensive 0 remove flag delete link

Comments

Rwadhwa910's avatar Rwadhwa910 (2021-08-17 08:59:17 -0600) edit
add a comment see more comments