resstock ashp capacity coefficients are all the same?

I am using resstock to generate building .idfs using air source heat pumps, but the idf's seem to all have the same capacity biquadratic curve coefficients. I've traced it down to resstock's source code, where it seems like they hard-code in capacity and EIR coefficients for all single stage heat pumps, regardless of efficiency or SEER.

Is there any way to get Resstock to generate capacity coefficients that match the sampled ASHP efficiency? Follow-up question, where can I find sample coefficients based on SEER/HSPF/Capacity?

zel3's avatar
83
zel3
asked 2021-08-06 14:48:38 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2021-08-06 17:17:12 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Most EnergyPlus performance curves are normalized. So the capacity and efficiency (COP) values will change based on SEER/HSPF/capacity, but the curves remain the same.

shorowit's avatar
11.8k
shorowit
answered 2021-08-07 09:29:04 -0500
edit flag offensive 0 remove flag delete link

Comments

Ah I see, thanks. So these curves are multiplied by the "Gross Rated Heating Capacity/COP" that are determined by the autosizing algorithm and the sampled efficiency?