Most Accurate way of totaling HVACTemplate:Ideal loads; Meter or Output Variable? [closed]

Hi All, I am trying to figure out the most accurate way of totaling the zone energy demand. I am asking because if I total the output variable for each zone using the "Zone Ideal Loads Zone Total Heating Energy Zone Ideal loads" I get a different heating energy use then if I looked at the "District Heating HVAC" meter.

Thanks,

Ross

Ross B.'s avatar
71
Ross B.
asked 2021-07-06 12:39:34 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2021-07-09 16:33:37 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by Ross B. 2021-10-27 08:12:32 -0500

Comments

add a comment see more comments

1 Answer

2

As you alluded to, when you use Ideal Loads Air Systems in EnergyPlus it applies all energy consumption to district heating/cooling. What you may be seeing in the difference between Ideal Loads Heating output variables and District Heating HVAC meter is the COP of the district heating. This can be set using the District Heating Efficiency input field of the EnvironmentalImpactFactors object.

You can read more details about Ideal Loads and District Heating in other posts here and here.