Does DCV/mechanical ventilation work for occupant count below 1 in EnergyPlus?

Hi everyone,

Does DCV work for occupant count below 1? for instance, when there is 0.5 occupant count, would there be mechanical ventilation?

Thanks

Wolfgang Kaiser's avatar
83
Wolfgang Kaiser
asked 2021-06-10 10:30:46 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2021-06-22 10:19:28 -0500
edit flag offensive 0 remove flag close merge delete

Comments

1

@Wolfgang Kaiser what simulation tool are you using? Please add a tag and/or mention the tool in your question so that others can provide better solutions.

Aaron Boranian's avatar Aaron Boranian (2021-06-10 10:39:27 -0500) edit

@Aaron Boranian I am using EnergyPlus itself not OpenStudio

Wolfgang Kaiser's avatar Wolfgang Kaiser (2021-06-10 11:09:36 -0500) edit
add a comment see more comments

1 Answer

0

The answer is Yes. Occupancy (number of people) does not have to be a whole number. EnergyPlus recognizes a small number or even less than one person (e.g., 0.5).