Heat pump cooling coil water flow

Can anyone tell me which parameters are controlling the v_dot_water request for the Coil:Cooling:WaterToAirHeatPump:EquationFit object? Or more specifically, should v_dot_water be a constant flow equal to the reference value, or should it be varying based on other operational parameters? And if it should be varying, which parameters are influencing that variation?

It doesn't seem to correlate well with any water or air temperatures or flows across the coil. I've also tried various setpoint managers on the water loop, as well as different design exit temperatures and design dT in the Sizing:Plant object, with no significant changes in the v_dot_water behavior. In my particular case, v_dot_water runs at either ~99.9% or ~85% of (hardsized) v_dot_ref, despite trying both Pumps:VariableSpeed and HeaderedPumps:VariableSpeed objects.

I've also checked the engineering and I/O refs, neither of which describe how the water flow request is being determined. I'm using e+ v8.7.

Thanks for your time!

codybond's avatar
371
codybond
asked 2021-05-04 13:31:00 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2021-05-20 17:36:07 -0500