1

Air extraction in wet rooms

Hello, in many buildings with natural ventilation is present an extraction fan in bathrooms, toilets etc... which don't have external walls but only share partitions with other rooms. Is it possible to simulate this? With the fan switching on when the room is occupied? I've used the "Fan - Zone Exhaust" but is not working

Thanks

Giorgio's avatar
55
Giorgio
asked 2021-02-25 14:46:47 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2021-03-15 11:53:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

@Giorgio to clarify, are you trying to simulate airflow from one zone into another zone that occurs with a fan only when one zone is occupied?

Aaron Boranian's avatar Aaron Boranian (2021-03-14 09:22:37 -0500) edit

Yes basically yes, image an extractor fan in a toilet without windows and connections with external walls, the air should move from the room with the window (let's say the hall) and go into the toilet for the extraction. The schedule should follow the occupation one

Giorgio's avatar Giorgio (2021-03-14 10:00:43 -0500) edit
add a comment see more comments

1 Answer

1

This process is usually called transfer air (air moves from one zone into another before exhausted outdoors). This post covers most of the modeling approach in DesignBuilder for transfer air.

To have the exhaust fan operate when the zone is occupied, you will need to do a few things:

  • set the System availability manager coupling mode input field to 2-Decoupled. This will allow the exhaust fan to operate independently of central system fans.
  • create a schedule with values of 1 when the zone is occupied and values of 0 for all other times, then assign that schedule name to the exhaust fan's Availability Schedule input field.
Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2021-03-15 11:52:06 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments