ASHRAE 90.1-2016 automatic baseline creation in OpenStudio

Hello, I posted a comment here https://unmethours.com/question/46754... since this question was somewhat related to mine but thought starting a new post may help in getting a response.

Does the 90.1-2016 baseline exactly follow the 90.1-2004 baseline? i.e. would following the suggestion from this post https://unmethours.com/question/46754... using the "Create Baseline Building" measure provide me with the 90.1-2016 baseline that can be used for LEED v4.1? Various sources refer to the 2016 baseline as "roughly equal" to the 2004 baseline, so wasn't sure if there was other modifications required to the 2004 baseline to get to the 2016 baseline. Thanks!

Phan Truong's avatar
161
Phan Truong
asked 2021-01-13 15:47:40 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2021-04-13 10:58:32 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

The 2016 Appendix G baseline does follow the 2004 90.1 requirements pretty closely, so that approach is generally appropriate. The existing Create Baseline Building does have some limitations, however. It is based on the DOE prototypes, and does not map the lighting requirements directly to the Appendix G requirements. If the space types in your model match those in the DOE prototypes, that will not be an issue. The measure also does not address several aspects of the 2016 Appendix G, including the latest window area requirements, special rules for laboratories and computer rooms, and the rotation through four orientations. The measure also does not create a proposed model, which might have some differences from the user model. An updated version of the Create Baseline Building measure for 90.1-2019 that will address these issues is under development.

Doug Maddox's avatar
76
Doug Maddox
answered 2021-01-14 08:15:36 -0500
edit flag offensive 0 remove flag delete link

Comments

Hi Doug, thanks for your response. We gave the measure a try, and it looks like there are some issues with assigning the correct system type. 90.1-2004 system type has slightly different building area requirements than 90.1-2016. Additionally, 90.1-2004 system type is based on heating source, while 90.1-2016 is based on climate zone.

https://ibb.co/5KdbbGx https://ibb.co/cYpJmDD

Any idea when the new measure for 90.1-2016 will be available?

Phan Truong's avatar Phan Truong (2021-01-18 16:00:39 -0500) edit