Comfort Analysis

I would like to evaluate the indoor comfort with OpenStudio. In particular I should evaluate the PMV index and the discomfort hrs (unmet load hours).

Is It possible with OpenStudio? Or do I have to use EnergyPlus? How should I do it?

Antop's avatar
353
Antop
asked 2015-05-12 04:29:51 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-10 21:00:34 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

In OpenStudio unmet load hours can be found in the EnergyPlus results at the end of the System Summary section (use Outdoor Air Summary hyperlink instead). There's also a nice measure to troubleshoot unmet load hours.

Results Summary tab > Reports > EnergyPlus Results

PMV can be added using the Predicted Mean Vote measure.

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2015-05-12 08:32:06 -0500
edit flag offensive 0 remove flag delete link

Comments

thanks these are the results that i can see. C:\fakepath\Untitled.png

the values within the last table are all zero. Why? are there no "unmet hours" ? is it possible I have forgot some settings?

Antop's avatar Antop (2015-05-12 10:13:45 -0500) edit

If your HVAC system is autosized then the unmet hours are commonly very low.

MatthewSteen's avatar MatthewSteen (2015-05-12 10:53:10 -0500) edit

Or in your case it looks like you're using ideal air loads.

MatthewSteen's avatar MatthewSteen (2015-05-12 12:50:58 -0500) edit