Positioning of pumps - plant loop/condenser loop

Hello!

Basically in energyplus we have loop pumps and branch pumps. Plenty of times in documentatios you can find applications with loop pumps on the inlet side. Is it also possible with energyplus to use multiple pumps (one pump for each chiller and one pump for each fluid cooler) on the inlet side or on the outlet side? Which pump obejcts are reqired (possible with Pump:ConstantSpeed and Pump:VariableSpeed objects)? Attached you can find the required chiller plant. 150506_Chiller-Plant.png

Thanks for your answers.

Best regards, Alex

nielex's avatar
139
nielex
asked 2015-05-06 11:32:19 -0500, updated 2015-05-06 11:45:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Is anybody there, who has tested or using fluid coolers and pumps on the inlet side or outlet side?

Regards, Alex

nielex's avatar nielex (2015-07-10 05:22:20 -0500) edit
1

Example file 5ZoneBranchSupplyPumps.idf illustrates branch pumps for each chiller. Similarly, branch pumps can be added with fluid coolers in condenser loop also. Two branch pumps i.e. both at inlet and outlet of chiller may not be allowed by EnergyPlus. Pump rules are summarized in the documentation.

Chandan Sharma's avatar Chandan Sharma (2015-07-10 07:51:48 -0500) edit
add a comment see more comments

1 Answer

1

Variable or constant speed branch pumps on each chiller are fine.

image description

Kyle Benne's avatar
6k
Kyle Benne
answered 2015-05-06 12:05:11 -0500
edit flag offensive 0 remove flag delete link

Comments

1

FYI, this will NOT work though if you are trying to set up a primary secondary pumping arrangement. See this thread

TaylorRoberts's avatar TaylorRoberts (2015-05-07 14:44:41 -0500) edit
add a comment see more comments