Humidifier latent only

I want to ask if there is a possible way -In EnergyPlus- where I can use a steam humidifier with no sensible heat addition.

Stay safe and Thanks in advance

Aly ElHefny's avatar
482
Aly ElHefny
asked 2020-10-06 17:00:40 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2020-10-07 12:00:30 -0500
edit flag offensive 0 remove flag close merge delete

Comments

@Aly ElHefny what simulation tool are you using?

Aaron Boranian's avatar Aaron Boranian (2020-10-07 11:25:50 -0500) edit

I'm using EnergyPlus

Aly ElHefny's avatar Aly ElHefny (2020-10-07 11:39:05 -0500) edit

Is this latent-only humidification at the same temperature (only moving straight up on the psychrometric chart) or adiabatic humidification that adds humidity and reduces temperature (move up and to the left along an enthalpy line on the psychrometric chart)?

Do you happen to have an image of the air state changes you want to simulate on a psychrometric chart that you can add to your post?

Aaron Boranian's avatar Aaron Boranian (2020-10-07 12:02:13 -0500) edit

It will be best if I can find a way to just add moisture with no heating or cooling ( humidify to a moisture content setpoint with no sensible heating or cooling)

Aly ElHefny's avatar Aly ElHefny (2020-10-07 14:36:59 -0500) edit
add a comment see more comments

1 Answer

3

Use an OtherEquipment object and specify 1.0 (100%) in the latent fraction field

UPDATE

Forgot to mention that Fuel Type should be "None". Like this:

OtherEquipment, 
  LatentLoad_Veg:Zone1, !- Name 
  None, !- Fuel Type 
  Zone1, !- Zone or ZoneList Name 
  latent_sched, !- Schedule Name 
  Watts/Area, !- Design Level Calculation Method 
  0, !- Design Level {W} 
  20, !- Power per Zone Floor Area {W/m2} 
  0, !- Power per Person {W/person} 
  1, !- Fraction Latent 
  0, !- Fraction Radiant 
  0; !- Fraction Lost

One more thing... My example adds only latent energy by selecting "None" as the fuel type, If you want energy to be consumed then a different object is needed.

Jim Dirkes's avatar
3.5k
Jim Dirkes
answered 2020-10-08 05:03:00 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2020-10-09 10:46:24 -0500
edit flag offensive 0 remove flag delete link

Comments

This would certainly work if you want to inject moisture directly into a zone. If you wanted to have an HVAC component meet a specific humidity setpoint within single-zone HVAC or a central air system, a different approach would be needed. @Aly ElHefny can clarify what they are hoping to achieve.

Aaron Boranian's avatar Aaron Boranian (2020-10-09 10:50:22 -0500) edit

Thanks a lot for the helpful answer.