5

Thermal Space Temperature unaffected by Sensible Cooling of VRF

Hello

I am modeling a single room that is cooled and heated by a VRF system. It has one outdoor unit and is connected to two indoor units that cool and heat the space. I have set up both units so that they begin cooling at 80 degrees F and begin to heat at 68 degrees F. The VRF system does begins cooling when the temperature goes above 80 degrees, but the rate at which the temperature increases seems to be unaffected. This is shown in the pictures below. I am unsure of why this is. Is the cooling capacity not large enough? I am fairly new to energy plus so any advice on how to trouble shoot this issue would be much appreciated.

Thank you!

image description image description

eklein12's avatar
373
eklein12
asked 2015-04-26 16:23:22 -0500
edit flag offensive 0 remove flag close merge delete

Comments

I think we would need to look at the particular model to figure out this one.

Kyle Benne's avatar Kyle Benne (2015-04-30 12:33:39 -0500) edit
add a comment see more comments

2 Answers

2

These results do indicate insufficient capacity to meet the load. Notice how the power falls off rapidly when the temperature is maintained at 26.7 C (80 F) and then falls below 26.7 C indicating that the load is also reducing. Without seeing the model inputs, I would recommend increasing the system capacity to see if that helps. Report back with the impact of this change.

rraustad's avatar
13.8k
rraustad
answered 2015-07-22 20:19:05 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

In general: Q = 1.08 * cfm * dT or DT = Q / (1.08 * cfm) So the change in temperature in the space is determined by both the cooling capacity and the supply flow. Sometimes increasing just the cooling capacity is won't solve the umnet load issue.

Chris Jones's avatar
1.1k
Chris Jones
answered 2015-07-23 07:15:29 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2015-07-23 07:21:22 -0500
edit flag offensive 0 remove flag delete link

Comments

Matthew, how do you find the time?

Chris Jones's avatar Chris Jones (2015-07-23 07:48:47 -0500) edit

Simple, @Chris Jones, I just decrease my time step ; )

MatthewSteen's avatar MatthewSteen (2015-07-24 08:06:17 -0500) edit
add a comment see more comments