how to estimate air change rate under natural ventilation mode

May I ask how to calculate air change rate under natural ventilation mode in OpenStudio, if a fixed air flow rate is not specified for the building?

I asked this because I saw in the following video that DesignBuilder has an option to switch between "scheduled ac/h" and "calculated ac/h" to estimate intensity of natural ventilation: https://www.youtube.com/watch?v=NS9ix...

So, can we do this also in OpenStudio?

Thanks!

oat's avatar
835
oat
asked 2015-04-25 02:39:17 -0500, updated 2015-04-27 11:40:22 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Please remember to add the software you are using to the list of tags. :)

__AmirRoth__'s avatar __AmirRoth__ (2015-04-25 09:50:43 -0500) edit

tag added as suggested.

So, any advice? Thanks!

oat's avatar oat (2015-04-27 11:58:36 -0500) edit

Do you solve you problem that the calculation of air change rate under natural ventilation mode

Done's avatar Done (2017-05-21 21:33:38 -0500) edit
add a comment see more comments

1 Answer

1

Natural ventilation is not yet supported in OpenStudio, however you might want to look into the EnergyPlus object named ZoneVentilationDesignFlowRate. This object is isolated well enough from other objects that it would be a good candidate for an EnergyPlus Measure in OpenStudio.

Kyle Benne's avatar
6k
Kyle Benne
answered 2015-05-04 11:54:49 -0500
edit flag offensive 0 remove flag delete link

Comments

noted with thanks, Kyle!

oat's avatar oat (2015-05-14 10:23:07 -0500) edit

Is there any update on this topic? It looks like that Openstudio 2.7.0, the one I'm using, has the natural ventilation feature. Would be good to learn more about it. Cheers

matteo-g's avatar matteo-g (2018-12-06 17:01:29 -0500) edit