How do I use advanced convection coefficient models in energyplus?

The drop-down menu shows TARP, SIMPLE, CeilingDiffuser, and AdaptiveCoenvectionAllgorithm for the SurfaceConvectionAlgorith Interior. But are there additional models available in EnergyPlus and can be used via IDF editor?

sajithwjay's avatar
445
sajithwjay
asked 2020-09-17 18:19:40 -0500, updated 2020-09-17 18:31:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The SurfaceConvectionAlgorithm:Inside object only has those four options. Is there a different algorithm that you would rather apply, or do you have specific convection coefficients that you want to apply each timestep?

UPDATE

You can set both inside and outside convection coefficients by timestep using the Energy Management System (EMS) feature of EnergyPlus. You would need to use the following EMS object:

See an example of these EMS objects below.

EnergyManagementSystem:Actuator,
  Inside_Conv_Coeff_Act,     ! Name
  East Wall,                         ! Actuated Component Unique Name
  Surface,                           ! Actuated Component Type
  Interior Surface Convection Heat Transfer Coefficient;           ! Actuated Component Control Type

EnergyManagementSystem:Sensor,
  Inside_Conv_Coeff_Sens,                      ! Name
  Convection Coefficient Schedule,         ! Output:Variable Index Key Name
  Schedule Value;                                   ! Output:Variable Name

EnergyManagementSystem:Program,
  Inside_Conv_Coeff_Program,         ! Name
  SET Inside_Conv_Coeff_Act = Inside_Conv_Coeff_Sens;

EnergyManagementSystem:ProgramCallingManager,
  EMS Manager, ! Name
  BeginZoneTimestepAfterInitHeatBalance,       ! EnergyPlus Model Calling Point
  Inside_Conv_Coeff_Program;                 ! Program Name 1
Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2020-09-17 18:32:48 -0500, updated 2020-09-18 11:08:29 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you very much for your response. That was my observation too. But if I can input convection coefficient by timestep that would be useful for me for the current application I am thinking of.

sajithwjay's avatar sajithwjay (2020-09-17 19:15:55 -0500) edit

Ah, I see. I've updated my solution to discuss how to set convection coefficients by timestep.

Aaron Boranian's avatar Aaron Boranian (2020-09-17 19:43:01 -0500) edit

This is incredibly helpful. I will try to implement and post my feedback. Kind regards,

sajithwjay's avatar sajithwjay (2020-09-17 21:32:18 -0500) edit

@sajithwjay Great! I forgot to mention one more EMS object that you will need, I've updated my answer accordingly.

Aaron Boranian's avatar Aaron Boranian (2020-09-18 11:06:58 -0500) edit

Thank you! I tried few combinations and saw that after errors are sorted the coefficient value still wasn't captured by the output. I will try this.

sajithwjay's avatar sajithwjay (2020-09-18 14:53:27 -0500) edit