4

Estimating plant size from annual energy consumption

This is more of an avoiding simulation question rather than how to simulate something. I'm looking at data on total annual heating/cooling energy consumption, and I'm wondering if there are any existing methods for estimating the plant size required for the building?

Jamie Bull's avatar
5.1k
Jamie Bull
asked 2020-08-13 03:28:57 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-08-16 16:24:51 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

Answering my own question to get this going. After a lot of searching, I found a procedure from a BRE report from 2016 that suggests I should be able to make an estimate based on annual energy use, plant efficiency, and equivalent full load hours (heating or cooling).

image description

I've also found another BRE report which gives cooling plant EFLH for offices in a range of UK cities.

image description

The calculation that makes sense to me is kWh / EFLH / SEER = kW

So, working that through, I find a (very approximate) installed cooling capacity of 138 kW.

         Annual kWh  EFLH   Efficiency   Installed kW
Cooling  455,895     1,500  2.2          138
Jamie Bull's avatar
5.1k
Jamie Bull
answered 2020-08-15 13:40:32 -0500