Outdoor Air Flow Rate of VRF systems

I built several VRF systems with DOAS using OpenStudio 1.7.0. VRF is used to deal with cooling/heating load, and all the fresh air from DOAS system. I tried to setup the "Outdoor Air Flow Rate During Cooling Operation" of vrf air thermail to 0 in OpenStudio, but when I came back, it will be "autosize" again. And simulation results showed that the outdoor air was double actullay, one from vrf and one from DOAS. I had to use text file editor to close the outdoor air of VRF. Is there something wrong? Thanks.

Yan's avatar
1.2k
Yan
asked 2015-04-20 13:13:27 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

I think you are hitting a GUI issue related to how the inspector works. If you click the radio button to choose "Hard Sized" and then leave that object and come back, it will have jumped back to "AutoSized". To make it stick you need to click "Hard Sized" and then click the cursor in the number field where the "0" is. Then if you leave the object and come back you should see the "Hard Sized" 0 stick, and your saved OSM should reflect that. Let me know if that doesn't address the issue.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2015-04-20 13:58:50 -0500, updated 2015-04-20 14:33:41 -0500
edit flag offensive 0 remove flag delete link

Comments

1

You are right, that solved the problem, thanks.

Yan's avatar Yan (2015-04-20 14:05:20 -0500) edit

This happens with all terminal units as well, not just VRF ones.

TaylorRoberts's avatar TaylorRoberts (2015-04-20 17:01:33 -0500) edit