How to reference OutdoorAir:Node using AvailabilityManager

In OpenStudio, I am trying to disable a cooling plant water loop based on outdoor air drybulb temperature using AvailabilityManager:LowTemperatureTurnOff. What node do I select to monitor outdoor air drybulb temperature?image description

Ski90Moo's avatar
869
Ski90Moo
asked 2020-06-09 11:26:01 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2020-06-09 14:58:55 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

You'll need to track down the name of the outdoor air node entering any central air system diagram. To do this:

  1. While viewing a central air system diagram in the HVAC Systems tab, click on the dot that represents the outdoor air node.
  2. See the name for the outdoor air node appear on the right side of OpenStudio.

image description

You can also update node names on the right after clicking on them in HVAC diagrams, in case you want to apply a naming scheme that makes sense to you instead of the default OpenStudio "Node X" numbering.