Energyplus output : surface window net heat transfer rate

I have modeled a building in Openstudio Sketchup (sketchup make 2016) and simulated in Energyplus to get the output of "surface window net heat transfer rate". I have plotted the monthly and hourly outputs and they shown west window gives higher output in winter months which is not reasonable. So that means the values are not correct. Can someone advice me how can I correct this?

Thanks!

Sachee's avatar
31
Sachee
asked 2020-05-22 22:30:05 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-05-23 12:33:16 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The Surface Window Net Heat Transfer Rate output variable is the sum of many components (transmitted solar radiation, convective losses, etc.), and positive values indicate heat flow INTO the zone through the window. To understand how the west window's net heat transfer rate could be higher in winter, you should add output variables for these other components (transmitted solar radiation, convective losses, etc.). Seeing trends in these components should explain the net heat transfer rate results, such as your building is in the northern hemisphere and excess solar gains at lower altitude angles in the winter are greater than the conduction losses to colder outdoor air in winter.

Aaron Boranian's avatar
14.1k
Aaron Boranian
answered 2020-05-24 07:59:34 -0500
edit flag offensive 0 remove flag delete link

Comments

As I understood, the definition of Surface Window Net Heat Transfer Rate output variable in energy plus is not correct. The result is not match the definition.

asro's avatar asro (2021-03-22 23:50:02 -0500) edit

@asro I've just posted an answer to your post on this topic here.

Aaron Boranian's avatar Aaron Boranian (2021-03-23 12:53:32 -0500) edit