Put the pump On and the chiller is OFF in the same loop

Hi All, I have a chilled water Loop consists of Chiller, pump and adiabatic pipes. Can I make the chiller OFF and let the pump working (ON)? When I use the SYSTEM AVAILABILITY MANAGER, all the loop will be On or Off! how to specify which equipment from the loop to be ON or OFF? Thank you

sergerwehbe's avatar
233
sergerwehbe
asked 2020-05-20 12:57:20 -0500
shorowit's avatar
11.8k
shorowit
updated 2020-05-20 15:25:58 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

What is you purpose?

With a Pump:ConstantSpeed you have the pump running even if there is no load on the loop and therefore the Chiller is Off. The Availability Manager Should be On. Be aware of the heat trafserred to the loop by the pump that could brings the temp loop over the max value and therefore causes a Fatal Error.

If you want to force the Chiller to stay Off even with a cooling load, you can use EMS forcing the Chiller branch flow to zero and all the flow to the by-pass (two parallel branches on the supply side sub-loop).

Ag's avatar
1.4k
Ag
answered 2020-05-21 12:38:57 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you. But if I forced the chiller branch flow to zero! The flow By the pump ( pump is ON ) still pass via chiller while the chiller is OFF? I want the chiller be OFF while the pump is ON and the pump flow enter the chiller without any load from chiller!

sergerwehbe's avatar sergerwehbe (2020-05-21 14:41:48 -0500) edit

In my vision is the same. What should happen, thermodynamically speaking, with the flow passing through the Chiller turned off rather than through an adiabatic by-pass pipe?

Ag's avatar Ag (2020-05-21 16:30:33 -0500) edit

I tried it. It’s working. Thank you