1

How can we measure the airflow rate from one zone to another zone in EnergyPlus in air changes per hour?

I understand that we have an output variable named "AFN Zone Infiltration Air Change Rate" which gives us the air changes happening in a zone because of natural ventilation from outside. However, I want to quantify the air that is travelling from one zone to another zone in air changes per hour. How can I do that ?

niharkopal's avatar
121
niharkopal
asked 2020-05-08 06:07:25 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

I don“t know if there is a output that gives the ACH, but you can use the output variable Zone Mixing Current Density Volume Flow Rate [m3/s]The air volumetric flow rate in m3/s entering the zone due to the sum of mixing, cross-mixing, andrefrigeration-door mixing during the hour or timestep using the density of air evaluated at current zoneair conditions.

Then you can convert the m3/s to ACH.

obuchely's avatar
1.4k
obuchely
answered 2020-05-08 08:25:03 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments