Adding multiple chillers in Design-Builder/Energyplus?

I added 4 additional chillers in HVAC design ( total of 5 chillers) in design-builder as shown in the figure below.image description

However, when I run the simulation in E+ and see the output file, I get 0 consumption from those additional 4 chillers ( check image below )image description

Can anyone help me why those chillers aren't working?

gopalchitalia's avatar
53
gopalchitalia
asked 2020-04-23 03:56:57 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-04-23 07:13:55 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Did you change the sizing fraction?

TomB's avatar TomB (2020-04-23 21:33:32 -0500) edit
add a comment see more comments

2 Answers

1

One thing to check is if all chillers have been added to the CHW plant loop at Plant Equipment Operation tab.

image description

Luís Filipe S.'s avatar
586
Luís Filipe S.
answered 2020-04-24 04:47:55 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

Tom's point is the most likely reason for only one chiller working. If you haven't already viewed them, I'd suggest you go through the free online HVAC tutorials here: https://designbuilder.co.uk/training/.... One of these covers chiller inputs. Also read the chiller information in the Program Help here: https://designbuilder.co.uk/helpv6.0/.... If you have a licence you can of course also ask our Support Desk for help here: https://support.designbuilder.co.uk/

Dave's avatar
1.6k
Dave
answered 2020-04-24 02:22:03 -0500
edit flag offensive 0 remove flag delete link