Fanger Model PPD output problems

I have a model with HVACs in EnergyPlus and i have this people objects : All peoples are in zones allDays until 24:00 , Fraction Radiant: 0.3 in all zones , Activity schedule: allDays until 24:00 with value 117 , Work efficiency:0.7 , Air velocity: 0.25 clothing factor 1 ,1 people per zone and i use PTAC HVAC the Zone Air Temperature change to the setpoint .I try 15 to 30 setpoints and the PPD comfort outputs is always 100% can help me anyone ?

Thanks

michalis Terzo's avatar
21
michalis Terzo
asked 2020-04-09 11:30:48 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-04-09 14:12:07 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Work efficiency 0.7 is not reasonable.

Usually it shlud be 0 or around it. It rapresent the mechanical work done by people, e.g. the difference in height going up the stairs that in a minimum part of the metabolic rate.

Plase see calc below (from Fanger equations), as example:

image description

Ag's avatar
1.4k
Ag
answered 2020-05-21 16:59:55 -0500, updated 2020-07-10 02:51:09 -0500