LEED ENERGY MODEL, number of chillers

Greetings,

We are working on a large project which has 10 customized Chillers each chiller over 2,000 tons.

When I model the baseline, the total cooling capacity is 32,000 tons which comes down to 40 chillers per Appendix G Table G3.1.3.7. Perhaps is there any exemption we might apply? We find a bit odd to model 40 chillers.

SantiagoSanchezSIMGEA's avatar
21
SantiagoSanchezSIMGEA
asked 2020-03-12 15:58:15 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-03-13 16:14:54 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

In my personal opinion, there is no exception to G3.1.3.7 in any version of 90.1 that has been published. It is odd to have to model 40 chillers but, I believe, that is the result of cooling capacity you found for your baseline.